§ 61.30-10 — -10 Hydrostatic Test
46 C.F.R. § 61.30-10
View:
All new installations of thermal fluid heaters must be given a hydrostatic test of 1
1/2 times the maximum allowable working pressure. The test must be conducted in the presence of a marine inspector. No subsequent hydrostatic tests are required unless, in the opinion of the Officer in Charge Marine Inspection, the condition of the heater warrants such a test. Where hydrostatic tests are required, an inspection is made of all accessible parts under pressure. The thermal fluid may be used as the hydrostatic test medium.